eglaude
Electrical
- Apr 1, 2004
- 19
I have a power system infrastructure that effectively puts two 3000kVA, 13kV/2.4kV, Z1=5.55% and Z2=6.33%, in parallel via basically a main-tie-main configuration. It's not as "clean" an arrangement, due to several feeder breakers that allow the tie between the two transformers. Old infrastructure flexibility.
Breaker coordination and selectivity is in general satisfactory, and typically the parallelling of these transformers is not done. We tie the two togehter when either of the transformers needs to be taken out for service.
We tripped one of the smaller feeder breakers when the busses were teffectively ied togehter even though the total currrent on both transformers were within the trip settings of the breaker. Typically our procedure calls to look for a split in current draw between the two transformers when a tie is made. Our systems are typically double ended and matched.
The mismatched transformer impedance is what I believe is causing the circulation current and resulting in a breaker trip of one of the in-line breakers that makes up the bus tie arrangement.
Can anyone give me some information on calculating circulation currents in mismatched transformers?
Thanks.
Breaker coordination and selectivity is in general satisfactory, and typically the parallelling of these transformers is not done. We tie the two togehter when either of the transformers needs to be taken out for service.
We tripped one of the smaller feeder breakers when the busses were teffectively ied togehter even though the total currrent on both transformers were within the trip settings of the breaker. Typically our procedure calls to look for a split in current draw between the two transformers when a tie is made. Our systems are typically double ended and matched.
The mismatched transformer impedance is what I believe is causing the circulation current and resulting in a breaker trip of one of the in-line breakers that makes up the bus tie arrangement.
Can anyone give me some information on calculating circulation currents in mismatched transformers?
Thanks.