I have extended our HV installation with one additional transformer 4,160/208 DY
A subcontractor is asking for some data concerning the LV part of the transformer – I think it is for the panels and other gear he wants to install.
I suppose he needs to know the maximal prospective short circuit current level Ik3ph. and a belonging X/R value – Do any of you now if this could be correct??
The only usable information I have found on the rating plate on the (used) transformer, is the value IZ 4.7% - 150KW
I think I’m getting old. I really can’t remember a lot of this stuff, maybe some of you could help me out.
1: The available data on the supply terminal is: The AC-Comp (7,779A) and the Asym (8,100A)
Which of this information will I use in my calculations (I think that it is the AC-Comp, the X/R value informs about the size of Asym, but I’m not sure about this)
2: The same data says that the X/R = 1.98, how can I translate this to useful X values and R values.
3: The 2-0-5KV cable is 120 ft. ( R=0.0764ohm/1000ft. and X=0.0414ohm/1000ft.). All right, I got that.
3: IZ 4.7% - 150KW on the transformers rating plate. Is that really enough information to calculate anything??
Thanks,
Lars