For relatively low shear loads, I've often argued that the shear load gets transferred through bearing between the column and/or base plate and the ground floor slab. However, I've been hesitant to rely on this mechanism for larger loadings (say > 50 kips) because I am unsure about all the necessary design checks.
AISC Design Guide #1 has a design example of this shear transfer mechanism and all they do is an allowable bearing stress check. Seems to me like you also might need to check in bending in the steel elements that are transferring the load.
What about further design checks on the concrete? Seems like there could be a breakout or bucking mechanism? Also, what if column blockout were used? Could the blockout pour fail somehow?
AISC Design Guide #1 has a design example of this shear transfer mechanism and all they do is an allowable bearing stress check. Seems to me like you also might need to check in bending in the steel elements that are transferring the load.
What about further design checks on the concrete? Seems like there could be a breakout or bucking mechanism? Also, what if column blockout were used? Could the blockout pour fail somehow?