I think kootk raises an excellent point that is perhaps not very clearly stated/covered in codes.
From most codes perspectives they state something like you only have an effective width of a wider beam at the joints and some of a wider beam might be considered ineffective (for both moment and shear). In ACI318-19 this is outlined in part in the dimensional limitations in CL18.6.2 (shown below). But for very wide beams that do not qualify with these provisions the code is a little silent. Clearly it can be wider, but not effective, but the question then is does it act like a two way slab, or other?
So they don't really cover to well is what to do if you want to consider the ineffective width on a wider beam as effective, for example you require the moment capacity of those bars right out on the edge of the beam to be effective, or to get the shear to work you need the full beam width considered and you might not meet the requirements of 18.6.2.
In this case you can use some judgement and detailing to add an orthogonal beam element to effectively pick up the shear from the ineffective part of the beam. In a way sort of like a corbel each side of the column but within the thickness of the beam, depending on the proportions you'd either design using strut and tie or normal flexural theory.
In your situation if you were following the ACI provisions to the letter, then with a circular column if you equated it to a square column of similar area to evaluate the dimensional considerations. Then the max effective beam width would be (1+0.75+0.75) x (π/6*350^2)0.5=775mm. So not all of the beam at 1000mm wide is effective. I'd make sure in this instance that you had sufficient orthogonal bars (and stirrups) through the column core in a similar manner to that shown in the figure below to pick up the shear outside the immediate width of the column (worked out on the basis that it is averaged over the width of the beam). This delivers the load to the column via this orthogonal beam element.
If you're just accepting that some of the beam is ineffective at the support, you need to be careful that you check the max shear provisions based on the effective width. In a way since part of the beam is considered ineffective the shear forces and moments concentrate into a narrower width at the column.