We have a main and alternate source transfer system utilizing two low voltage power circuit breakers. We are having an ongoing discussion as to whether or not it is desirable for the automatic transfer scheme to close the alternate source circuit breaker if the main source breaker trips due to overcurrent.
One side says transferring will improve reliability because the main breaker might have a nuisance trip or the fault may be momentary. The other side says it will reduce reliability because of the possible increased equipment damage and will increase hazard to personnel. This is a "high up-time" facility. The alternate source is a diesel generator.
Does anyone know of any standards or codes pertaining to this question? NEC Article 430 prohibits reclosing faulted motor circuits, but doesn't address other situations.
One side says transferring will improve reliability because the main breaker might have a nuisance trip or the fault may be momentary. The other side says it will reduce reliability because of the possible increased equipment damage and will increase hazard to personnel. This is a "high up-time" facility. The alternate source is a diesel generator.