Yes, H-W Operator interface can display trend screens in one of 2 modes.
Note: Trending is not associated with data stored on the floppy or ZIP drive.
Data stored on floppy or ZIP can only be viewed with PC software, not on the O/I.
Mode 1 - Single loop faceplate with loop trend screen,
Operator Interface User Guide 51-52-25-108; pg 142 (pdf)
If memory serves me, this is a 15 or 30 minute trend screen for which there is no cache memory, the implication being, that if the operator changes the screen to something else and comes back to the trend screen, the trend screen starts over again, there is no residual trend from the previous screen. The trend starts every time the screen is accessed. There is no scroll back, so the visible time domain is a moving 30 minute window: from NOW to 30 minutes ago. The intention was to use it for tuning a loop.
These screens are not 'configured', screens become available when a loop is implemented.
Mode 2 - Monitoring historical trends
samples and descriptions of the various trend screens are described in the Operator Interface User Guide 51-52-25-108, starting on page 281 (pdf)
Trends data is saved in memory (not the floppy or ZIP drive) so that whenever any screen is accessed it populates with historical data.
These display screens need to be configured (activated and populated) in the development software, Hybrid Control Designer (HCD). The HCD manual is 51-52-25-10
for historical trending see:
pg 72 Operator Panel Worksheet Overview
pg 74 Trend category
pg 77 Trend Display Tag Groups
Dan