3doorsdwn
Structural
- May 9, 2007
- 162
The 13th edition now addresses bracing strength (and stiffness) for points along columns and beams. For beam bracing, criteria for lateral bracing and torsional bracing are given (as opposed to using some of the old rules of thumb (i.e. 2% of the compressive force, etc.)). My question is: If my section (a doubly symmetric I-beam) cannot fail by flexural-torsional buckling (only by flexural buckling), does torsional bracing need to be considered? Or just lateral restraint for the compression flange?
Most I-beams (in the steel manual) are controlled by flexural buckling (at the typical lengths used in design). So I was uncertain if they meant this criteria primarily for singly symmetric shapes, or was it intended to take care of initial twist imperfections in the beam.
Any thoughts are appreciated.
Most I-beams (in the steel manual) are controlled by flexural buckling (at the typical lengths used in design). So I was uncertain if they meant this criteria primarily for singly symmetric shapes, or was it intended to take care of initial twist imperfections in the beam.
Any thoughts are appreciated.