Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Torsion in a simply supported beam

Status
Not open for further replies.

allimuthug

Civil/Environmental
Oct 5, 2014
142
Hi,

Torsion_e7egsm.jpg

I have a simply supported I-beam, connected by fin plate connection. Will this beam can take torsion.
As per AISC design guide 9 simply supported beam takes torsion. According to me this beam will never take torsion.
Please correct me.
 
Replies continue below

Recommended for you

There will be some torsion - but only to the extent that the single plate connectors can resist. They probably have very little torsional stiffness so there would likely be minimal actual torsion in the beam.


Check out Eng-Tips Forum's Policies here:
faq731-376
 
The beam can take the torsion.....the ends (likely) can not. I did a study on this some years back: You typically need some type of flange restrained connection (i.e. moment; torsionally "fixed") to transfer a significant amount of torque (unless you have some intermediate/sub framing that won't let it get to the ends).

Basically with clip angle/single plates.....the torsion will go to the connection by bending in the web. The web typically can't take much.
 
This is what you would call a torsionally pinned end. Yes, the beam can take some torsion.
 
"torsionally pinned" = it doesn't work ?

I think the clips can carry the incidental torsion that arises due to small imperfections, but not any sizable torsion like from a load.

another day in paradise, or is paradise one day closer ?
 
Status
Not open for further replies.