Double Angle Connection with Torsion
I'd like to bring this question back up:
http://www.eng-tips.com/viewthread.cfm?qid=266236
I'm trying to get a list of checks for this situation. Especially for the beam web and double angles.
For the beam web, can you simply add shear stress plus torsional shear stress?
For the double angles - BA suggests a T/C couple and checking strong axis moment, but this sees odd to me as the angle is fastened to a support and you would probably get a significant amount of capacity. Checking the legs as tall thin rectangles in torsion seems pretty conservative. Breaking the torsion up into a T/C couple as M/(L.angle/2), then checking half the angle as "flange bending" seems like a possibility but also kinda odd.
Any thoughts?
Thanks in advance!
Any thoughts?
Thanks in advance!
RE: Double Angle Connection with Torsion
Ergo, you can't use this type of connection to transfer any significant torque. You have to either: change the connection type or you need to have beams framing into the torqued beam (on each side of the torque) and take it out that way. (Which you can do even with a simple shear connection. You just have to model it with a (flexural) fixity of maybe 10%.)
In my case the beam web is pretty thick (>1"). But the angles are not (5/16"). Any suggestions on the effective width of the angle?
Thanks again.
EIT
www.HowToEngineer.com
Assuming you are talking about the force distribution (from the force perpendicular to the angles)......I typically assume a triangular distributed load. (See pic below.)
By the way, if you run with this, keep in mind (for the "stick" model): the end torsional fixity isn't going to be 100% fixed or free. Estimating that is important to determine rotation. In the study I mentioned in my first post, I typically got conservative (i.e. higher than theoretical) rotations by releasing just 10% of the fixity. However, that probably will vary from beam to beam based on web stiffness.
By the way, in my pic, I don't show a cope.....if you've got one....you've got issues trying to get this out of the beam.
Regarding the angle -
I was talking about the force perpendicular to the web applied to the outstanding leg of the angle. I was thinking about checking the outstanding leg in bending. I was only thinking about using an effective width equal to the length of the out standing leg.
EIT
To go with your mark-up....I'd take "beff" to be "d/2" (my notation; i.e. half the angle depth of one angle).....with the load distributed as I show it.
EIT