Hello, I have a question regarding a typical 51 element's response to a decaying AC current.
If I were to have a decaying AC (no DC or asymmetrical component) current and a standard ANSI inverse overcurrent element, would you assume the best way to calculate the time to trip is using an iterative approach in excel? Is anyone aware of any formulas or rules-of-thumb for time-overcurrent element response to time-variant current?
For example, if I had a linearly decaying fault current, I would calculate it by using very small time intervals and iterating as follows:
1. Using small time intervals such as 4.1667ms (1/4 cycle), calculate the time to trip at that current value (lets say 1.5s at this current)
2. Divide the time interval (4.1667ms) by the time to trip (1.5s) to get the percentage of total time to trip for this interval.
3. Doing the same calculation in the next row, add the previous row to this row to acquire the cumulative % of time to trip.
4. Continue the iteration until the cumulative percentage reaches 100%. At this point, if you were using a time-invariant (constant) current value, the cumulative time to trip (total sum of time intervals) would equal the time to trip as calculated by the ANSI 51 element formula.