The biggest telling clue is this:
6 inches/hour and references the 24 hr/25 year storm event
Really? 6 inches per hour over 24 hours is a 144 inch storm. Which is nonsense. The appropriate units for I in the rational method are inches per hour, not inches. They probably saw that there were 6 inches (not in/hr) in a 24 hour storm for their region, and then decided to use 6 in/hr as their I by just arbitrarily changing the units. Then since they had magicked up their I without actually calculating a Tc, they probably said "it can be neglected" because they didn't know what else to say.
I agree with some of the above posters. Tc calculation is often so arbitrary anyway that for smaller basins it's conservative to just go with a minimum, usually 5 or 10 minutes, and pick their intensity off an IDF curve or from a published table. If they do this, a reviewer shouldn't have a problem with it, although I must admit I've been raked over the coals by picky reviewers for assuming a minimum Tc without providing a backup calculation. One job I had to provide 20 Tc worksheets each showing a Tc of 3 minutes or less, to justify to the reviewer my choice of picking 5 for each basin.
Tell them to pick a Tc and pull their I off an IDF curve. If they don't know what you're talking about, then go through all their work with a fine toothed comb. I'm sure plenty of engineers here on Eng-Tips would love to do so for you on a contract basis, just to have some fun stories to tell their friends.