Tilt Panels out of Plumb 1

Status
Not open for further replies.

lesmcg

Civil/Environmental
Feb 17, 2002
3
I have a contractor who has placed panels up to 4 inches out of plumb. Panels are 26 feet high. Has anyone a reference to an acceptable out of plumb tolerence for panels?
 
Replies continue below

Recommended for you

Fig 4.6.9 Erection tolerances, architectural wall panels

1 inch, maximum plumb variation over height of the structure or 100 ft, whichever is less.

at p. 230 in

Architectural Precast Concrete
2nd edition
pci Precast/Prestressed Concrete Institute
Chicago 1989
 