x5bulldog
Structural
- Jan 8, 2008
- 27
I have a question about the tie spacing / transverse reinforcment in piles. I am in a low seismic Region so chapter 21 of the ACI 318 does not apply to me. Also ACI 318 states in chapter 1, that ACI 318 is not for piles unless for high seismic regions.
From ACI 543 in the Structural Design Considerations Chapter that "PILES THAT HAVE SIGNIFICANT BENDING MOMENTS WILL OFTEN HAVE SIGNIFICANT SHEAR FORCES" Chapter 11 from ACI 318 should be followed when designing shear Reinforcement.
What is SIGNIFICANT? Spacing limits for shear reinforcement is d/2 ; that seems intense to me for a pile. With the loadings I have on my piles the Concrete strength (Vc/2) can almost take all the shear. I can be less conservative and reduce my shear.
Again what is significant 5 kips, 25 kips, 50 kips of shear??
Someone can argue that 1 kip or 2 kips of shear is significant and that I have a significant bending member and must use d/2 for my tie spacing.
From ACI 543 in the Structural Design Considerations Chapter that "PILES THAT HAVE SIGNIFICANT BENDING MOMENTS WILL OFTEN HAVE SIGNIFICANT SHEAR FORCES" Chapter 11 from ACI 318 should be followed when designing shear Reinforcement.
What is SIGNIFICANT? Spacing limits for shear reinforcement is d/2 ; that seems intense to me for a pile. With the loadings I have on my piles the Concrete strength (Vc/2) can almost take all the shear. I can be less conservative and reduce my shear.
Again what is significant 5 kips, 25 kips, 50 kips of shear??
Someone can argue that 1 kip or 2 kips of shear is significant and that I have a significant bending member and must use d/2 for my tie spacing.