Tie force (can it be greater than shear force)?
ajay__re
5
Can tie force calculated using the formula from EC 1991-1-7 be greater than shear force? Is it stated somewhere in the codebook that the tie force should be lower than or equal to tie force?
-Thanks
Dear ajay__re (Structural),
EC 1993-1-7 is for Strength and stability of planar plated structures subject to out of plane loading..
Not sure for the which formula stated in EC 1993-1-7..
Will you pls be more specific?
I could not look to your post yesterday...
You know EC 1991-1-7 is for Accidental actions and the subject formula is at annex A ; Design for consequences of localised failure in buildings from an unspecified cause and ANNEX A is not normative..
I have copy and pasted the formulas below,
Notice that the design tension force is some portion of gravity loading ( 0.8 for internal ties) and the design tie force( Ti )
calculated using the above would be greater than the shear force..
there are worked examples for Ti calculation at annex A..
If this a real question, you may post some sketches to get numerical responds..
If shear force is say 10kN, and the minimum tie force is 75kN, then the tie force is greater than the shear force.