If you are talking about the pre-engineering building, I would say the pre-engineering building vendor always assumes the column base is PIN with zero deflection.
In the reality you have some deflection, that would cause some lateral load and member force deviating from the result getting from model using ideal PIN assumption, but for most of the time PIN base assumption shall be OK.
Ideally you shall calculate your base stiffness with spring in 3 directions, kx, ky, and kz, and pass these foundation stiffness to the building vendor so they can plug in their model and work out a more accurate result for you.
When you work out the foundation stiffness, you shall consider the concrete pile or pedestal’s cracking EI, with around 0.5EI to be more realistic, and apply the pile group facto as applicable. Just roughly estimate the lateral load (wind or seismic) at each column base and workout the deflection to get the stiffness = P/delta. You can safely assume these stiffness k are linear in a small deflection range.
I would say none of the pre-engineering building vendors I worked with before asked for the foundation stiffness and all of them just assume all column bases are ideally PIN.
I worked with Krupp on many heavy mining machinery and equipment and Krupp always asked the foundation stiffness. With the foundation stiffness plug in you will get the accurate support reaction and frame member forces.