elektroeng
Hi Gents,
We are going to install a gas turbine in our refinery (36kV infeed and 6kV distribution with 15MW peak load and two transformers 36/6kV, one 15MVA and one 25MVA) with a power of 14,5MW. This transformer needs an insulation transformer to reduce short circuit power added to the 6kV network and to insulate from high earth fault currents (700A with two transformers parallel). Now my idea was to replace the 15MVA transformer with a three winding transformer :
- 1 36kV side 25MVA with load tap changer controlled by the 6kV voltage
- 1 6kV side 25MVA (parallel with existing 25MVA)
- 1 10kV side 20MVA (GT connection)
What do you guys think of this scheme ? Are there things that i have to take special attention of ?
Thanks for your suggestions.