More information on the sketch would be helpful. I assume that the soil behind the 2 parallel walls slopes down from full height at the left end to about nothing at the right end. If so, you will get little (probably insufficient) shear resistance from the parallel walls, especially if these 2 walls deflect toward each other. There isn't a good way to design this as shown. It MAY work if you have enough, reliable, soil cohesion and the soils therefore can stand unsupported as long as needed.
Can you install a single straight wall with a wale and at least two, inclined, raker braces to concrete heel blocks in the approximate locations of the 2 parallel walls? The 2 parallel walls would not be needed if you can safely slope downward from the left wall.
See sketch.