strucuturesareus
How would you deal with thermal movements in large building structures? Would you reduce the 'design' movement for the moderated temperature of an enclosed building? Would you attempt to calculate the net temperature of the structure considering the daily thermal lag (ie, peak daily temperature is greater than peak structural temperature)?
Would you allow movements of the structure during construction and then lock in the connections after the building is heated?
We are working through the analysis of a large format structure for thermal movements. It is about 600 ft square to be built as a single unit - steel upper portions and concrete lower. There are internal parking decks that are exposed to the exterior. Temperature variations amount to about 95 degrees in this location.
To handle the total potential thermal movement, this building would have troubles. However, thermal lag between overnight and daytime temperatures at both cold and warm days could reduce thermal variations significantly.
Once the building temperature is stabilize during its service, the real movements due to external temperature swings will be controlled. Is it common in design to account for reduced thermal temperature swings as a result of controlled internal temperature of the building?
If so, then we need to determine the net average temperature within the structure. A thermal variation within a structure between exposed (or insulated exterior) structure and the internal surface temperature results in a net average structural temperature. This variation could substantially reduce the actual movement that the structure must undergo. Has anyone a reference to methods of analyzing this temperature variation?
Thanks for your help!