Paresh
I have also been involved in similar projects in the Middle East and have some real horror stories as to what end users, consultants and drives companies DO NOT know and try to do thinking they know better (a real case of a little knowledge is dangerous !!). Price, not safety is usually the main criteria. I still do consultancy on drives and harmonics in that area now, both in hazardous areas and general applications.
I will try and answer you questions as follows :-
1. No there are no real guidelines (as far as I know) for dv/dt other than minimise it. Older VFDs did tend to be bad but IGBT ones which switch up to 8-16khz have steep dv/dt too. 600 V/uS and upward can cause real problems on the winding insulation, especially on older motors or those with Class B and less insulation (E).
2. Current source inverters are kinder to the motor as they do not cause as high losses. The problem is the CSI are not 'sexy' and cannot be mass produced at low prices. CSI require the motor to have high levels of magnetising current as it is this which commutates the inverter output bridge; so motors and converters have to be matched closely. Such close matching is not a usually a requirement of PWM drive which introduce additional stator and rotor heating to the motors. This can be attenuated by high quality sinus filters but these are expensive. Also with CSI the displacement power factor varies with speed and load (displacement pf is the pf without the harmonics). PWM drives have a dpf CSI harmonics are not as 'stair cased' as PWM).
3. My experience is that CSI is better with ex motors, but more expensive and not feasible at all at smaller powers (<300kW). I am talking here about new installations where the ex motor/VFD was supplied at a certified and fully tested package. Suggest you look a
for info on this as they do PWM to 500kW and CSI to 8000kW for gas, oil and petrochemical industries. They are one, if not, the best in world in this area.
One crucial fact here re CSI or PWM is that whenever you retrofit an VFD to an ex motor your motor certification is no longer valid as the motor will "operating outwith the conditions envisaged when it was certified". If this is an explosion due to the motor the industrial insurer may not pay out if it is proved the use of uncertified equipment was the cause. Do not take this lightly please ! Fitting sinus filters will make no different legally!
4. CSI drives do not require sinus filters but you have to consider the voltage commutation notches on the motor (every 60 deg). If a new application this can be optimised via carefull motor and inveryer output bridge capacitor design. It is usually well within the capability of the motor insulation.
I would not recommended retrofitting CSIs to ANY application (never mind hazardous area - as per the comments above)without careful consideration of all the motor and application (starting torque, etc) issues. I would approach Loher, Siemens and others; high quality CSI manufacturers for advice.
Paresh, I have a couple of papers which WILL be of interest to you. If you want to email me seperately on mailevans@tiscali.co.uk I will send them to me; they are not for open distribution. If you have any other specific questions use the same address.
I hope I have helped. The advice about NOT retrofitting VFDs to ex motors in the most important here !
ICEMAN