The magnetising current inrush in a transformer is rich in 3rd harmonic?
yes or no?
yes or no?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
The spreadsheet is a tool/model for consideration. I think the contents (model) is pretty transparent, but then again I wrote it. Even without the any computer aides at all, I think we can easily say the typical inrush time waveform with sharp repeating peaks every 1/60th of a second will fourier transform into harmonics of 60 hz generally starting highest at 1st and decreasing from there including both even and odd harmonics. The spreadhsheet graphically illustrates this. How exacting an analysis is required to quantify these results and their variability depends on your purpose (I have no intent in investing time on it).I like to see trends rather than a single example. When dealing with non-linear issues, a single example may be misleading, unintentionally of course.
Areva / Alstom "Network Protection and Automation Guide" said:"Typical inrush currents contain substantial amounts of second and third harmonics and diminishing amounts of higher orders."