texasmike45
Mechanical
- Oct 6, 2004
- 15
I have a couple questions about how other boiler users interpret section 755.026 of the Texas Boiler Law copied below. I realize TDLR and the insurance inspector have the final say so. I am mainly curious as to other users opinions and practices.
(1) Assuming section 755.026 is complied with can the internal inspection of a power boiler be extended to the full 60 months even if the boiler is shut down within the 60 month period for other maintenance activities?
(2) For unfired steam boilers and steam collection drums could the "next scheduled down time of the boiler" be the 84 month or 120 months allowed even if the boiler is shut down for other maintenance work?
§§ 755.026. EXTENSIONS.
(a) With the approval of the executive director and the inspection agency that has jurisdiction for the power boiler, the interval between internal inspections may be extended to a period not exceeding a total of 60 months. For unfired steam boilers or steam collection or liberation drums of process steam generators, the inspection interval may be extended to the next scheduled downtime of the boiler, but not exceeding a total of:
(1) 84 months for unfired steam boilers; or
(2) 120 months for steam collection or liberation drums of process steam generators.
(1) Assuming section 755.026 is complied with can the internal inspection of a power boiler be extended to the full 60 months even if the boiler is shut down within the 60 month period for other maintenance activities?
(2) For unfired steam boilers and steam collection drums could the "next scheduled down time of the boiler" be the 84 month or 120 months allowed even if the boiler is shut down for other maintenance work?
§§ 755.026. EXTENSIONS.
(a) With the approval of the executive director and the inspection agency that has jurisdiction for the power boiler, the interval between internal inspections may be extended to a period not exceeding a total of 60 months. For unfired steam boilers or steam collection or liberation drums of process steam generators, the inspection interval may be extended to the next scheduled downtime of the boiler, but not exceeding a total of:
(1) 84 months for unfired steam boilers; or
(2) 120 months for steam collection or liberation drums of process steam generators.