The resistance to ground of a ground rod, ground grid, or any buried metal item is typically measured using a three-point, Fall-Of-Potential test, where two test rods are placed in a straight line out from the equipment under test. The typical distance is 100', which usually suffices for a single ground rod, or maybe three within a few feet. The distance is based on the size of the grid under measure, and may have to be much more if the overall grid size is large. Once the furthest rod (C2) is placed, the other rod (P2) is placed at 61.8% of that distance, in a direct line between the C2 and the rod under test. The P2 rod is then moved to 2-3 locations closer and 2-3 location further than the 61.8% distance. The result from each point is then tabulated and the graph drawn will show if the result at 61.8% is correct, or if you need to move the C2 rod out further to get out of the 'Sphere of Influence' of the rod under test. These tests are best conducted by a NETA trained technician/engineer, who is familiar with the procedure.