In a power plant environment, what type of test are required before reconnect the generator to the grid in the event of a fault located between the main transformer (GSU) and the HV switchyard?
 
Replies continue below

Recommended for you

HV generator?

If there was no electricity there would be no internet. Good point, don´t you? :D
 
Here are more detail information.

System Description: There is three generators, with total capacity of approximately 800 MVA,18kV connected to 3-GSUs (Generator Step-up Transformers) 18kV/345kV interconnected to a single 345 kV bus and then connected to a ring bus switchyard 345 kV via a single T. Line (approx 1 mi).

Predicated fault: A fault in the 345 kV will stress generators, GCB, GSU, etc

Usual Practice after fault: I know general utility practice do not reclose on transformer and UG cable faults until a maintenance crew verify that there is not permanently damage if they re-energize.

Rational: I presume that similar procedures are used in generator and other important equipments after fault. I am curious about type of test and typical duration or rought downtime per generator if available.
 
OK, but how does it work? three fulltime? one or two stand-by?. Fault triggers all breakers, generators stop. If selective coordination works i think you only have to check protections, if it is a full time systems that the best chance to inspect everything.

If there was no electricity there would be no internet. Good point, don´t you? :D
 