Thank you all for your kind help and replies.
I have finished the design of the building.
I talked to a gentleman from technical support, and this is what he suggested and I concur:
Model the X bracing in RAM. Since it's a rod, I need to go to the master steel table, i.e. aisc.tab to add some rod properties in - "ROD0.5XROD R 0.500 0.250 0.196 0.003068 0.012272 0.020833" This is a 0.5" dia. rod. In RAMFrame, I will assign a very small K to the X bracing, like 0.1, so that compression force will not govern and the rod will only be checked against the tensile force. This is one of the option.
The other option is to model only 1 side of the X bracing in with small K value, and design them. And run another design with the other side. The largest size shall be the design.
Although this may sound troublesome, but I think it's the right way to do it. Hopefully, the new RAM will accomodate this problem.