Hi waross,
It's European terminology. TT is an abbreviation for Terra-Terra. The source is grounded to a local earthing electrode or mat. The customer has a similar electrode at the service intake and there is no metallic ground connection between customer and source. Earth loop impedances are typically high and require use of an RCD as the intake switching device.
Other related European terms are:
[ol]
[li]IT (Isolated-Terra) for ungrounded sources with an earth electrode at the customer intake.[/li]
[li]TNC (Terra-Neutral Combined) for a metallic combined earth and neutral conductor connected to an earthing elctrode at the source.[/li]
[li]TNS (Terra Neutral Separate) for a metallic earth conductor, separate from neutral, connected to an earthing elctrode at the source.[/li]
[li]TNC-S (Terra Neutral Combined-Separate) for a combined neutral and earth up to service entrance connected to an earthing elctrode at the source, with separate neutral and earth conductors available at the customer's intake.[/li]
[/ol]
TNC-S is frequently seen in the UK as Protective Multiple Earthing or PME. PME allows the distribution company to effectively earth the neutral conductor throughout its length as well as at the substation earth mat, saving the cost of running a separate earth conductor.
----------------------------------