Temporary power drop discussion 3

Status
Not open for further replies.

itsmoked

Electrical
Joined
Feb 18, 2005
Messages
19,114
Location
US
I have a big generator that's costing $8,100/mo to rent.
$150/mo fee for the CA air quality board.
$4,400/mo fuel.

Waiting for the new power drop from the POCO will take at least 8~9 months.

We're searching for a solution to the $12,650/mo pain.
The generator panel has never shown more than 50A @ 480V.

I have a power pole field drop with 200A 240V delta service barely used, a couple of lights.
One way distance is 750ft.
I have a 240/480 50kVA transformer.
2 AWG will cause a 2% drop carrying 50A.

My biggest concern is motor starting. I don't yet know what the largest motor is that needs to be supported. From memory I don't think there's probably one bigger than 15hp/480v but I'll have to check later today.

What do you think, doable?

If you think this can work, do you have any suggestions for 'cheap' cable or wire? This is all temporary.


Keith Cress
kcress -
 
If the cable has a J in the type, it is only rated for 300 volts.
 
Sorry for doubting you on that Keith.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 