Comment on electricpete (Electrical) Jul 24, 2002 marked ///\\jbartos - In case you haven't figured it out yet, the oversizing arises from the fact that class F insulation is installed, but it's temperature rating is not used.
///Yes. This is correct. That is why you have to in your posting increase the size of F insulation class generator power rating to be able to supply the same power as the B insulation class generator. This still appears to be due in your postings. I have concentrated on the tgott july 23, 2002 posting first since there were some errors but it captured a correct idea that the generator resistance will vary with the operating F insulation class generator downsized to B insulation class generator. Then, obviously with the upsizing the F insulation class generator power, the R of windings will be somewhat smaller.\\\
The copper temperature coefficient of resistance is not what creates the oversizing (margin).
///Yes, this was never disputed anywhere.\\ In fact if anything it slightly reduces the factor by which the system is oversized.
///This remains to be expressed mathematically.\\ Proof.... Ask yourself the question: how much higher could I increase load if I took full advantage of the class F insulation rating.
///The tgott posting on July 23, 2002 considered F insulation class generator power upsize to meet the B insulation class operational requirements based on resistance changes while the current changes were not considered. This is obviously inaccurate, since the major variable is neglected.\\ You will come up with a smaller increase if you consider the temperature coefficient than if you don't.
///This remains to been done and seen.\\