I don't mean to be a wet blanket here, but that is going to be a near impossible task. I have done a lot of work on electronics in sawmills; maintaining that narrow of an environmental spec is going to cost you more than the equipment is likely worth, and keeping it running for any appreciable length of time is not likely. Two factors will come into play:
1) Any enclosure that is going to keep out sawdust is going to need to be NEMA 12 or better. That means no air exchange whatsoever. A sealed box then is going to require air conditioning, such as a
Hoffman /
McLean industrial AC unit. The trouble with that is, they have an outside air circulation system for the evap coils and those have filters on them to prevent contaminant loading of the coils. In a sawmill, NOBODY will clean those coils after the first month of service and in 6 months the AC unit will overheat and die. It's just an inevitability.
2) Humidity will be a problem if you are looking at the arid eastern BC (Kelowna, Okanogan, Penticton etc.), and winter temperature will be a problem on the west (wet) side and north. East side will have days in the summer where the ambient RH will be as low as 20% already. Those will also be days where the temperature will be highest, so the AC will be running full blast, dehumidifying the inside even more. I have seen static destroy sensitive electronics in areas like that almost as much as heat. Remember, you can
de-humidify electronics, but you cannot humidify them if they are too dry. In the west and north, your enemy will be extremely low temperatures in winter. They don't shut the mills down up there, they like to think of themselves as a hardy bunch. But when you run the AC to dehumidify, you will need a big heater to keep from freezing the insides as well. The balancing act can be very tricky to maintain. I have seen several systems fail to keep it consistent enough to survive for long.
My suggestion would be to rethink your electronics design. Most industrial electronics based systems need to be able to tolerate 40C as a minimum upper range, 50C is better and 60C is the gold standard. You lower range also needs to be capable of 0C operation and -10C storage, otherwise you will have a big problem when they power up after a power failure. RH specs tend to be 10 - 95% so as to tolerate being operated in air conditioned enclosures, but if you can get the temp tolerance higher, it also allows the use of heat exchangers that are not as prone to failure as AC systems in sawdust environments (but do not de-humidify). Conformal coat your boards to survive the humidity, heat sink all of your sub-assemblies and high power components to increase the temperature tolerance. Also, make sure you have a stout power supply section (or a good external PSU), because the line power has a lot of nasties in sawmills.
Good luck.
"If I had eight hours to chop down a tree, I'd spend six sharpening my axe." -- Abraham Lincoln