Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Temperature Effect On NGR sizing

Status
Not open for further replies.

ohms

Electrical
Jul 24, 2004
17
Apart from the standard NGR sizing calculation, do we need to take account the effeect of temperature on NGR sizing as well.

Thanks if someone can guide me to calculate this factor.

 
Replies continue below

Recommended for you

If you are talking about ambient temperature and a 10-second resistor rating, I'd say no.

What type of temperature are you concerned about?
 
ohms:

You may follow this link,
They provide better literature to your query.






"Whenever you are asked if you can do a job, tell them, certainly I can! Then get busy and find out how to do it." Theodore Roosevelt.
 
Yes, ambient temperature.
I used the standard temperature coefficient to evaluate the inrease in resistance and therefore the current limit.
NGR is rated for 25C and ambient is 50C.

But the effect is negligible.
 
Grounding resistor are rate by IEEE std as follow:

1) Ambient temperature: < 40°C and the
2) average temperature: < 30°C for cooling air for any 24-hour period.

3) The altitude does not exceed 3300 ft (1000 m).

CLARIFICATION: For GND resistors rated for typical temperature rise of 375° ,610° or 760° C, a few degree above the rated ambient temperature may not have significant impact on the equipment performance. However, if the temperature is unusual high, this need to be checked
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor