This is a common configuration and is an energy hog. The chilled water wrings out the air by using a lower discharge temp setpoint. On hot, humid days, the 100% outside air unit can be set to discharge at a real low temp (say 50°F, as long as it's sufficiently designed) - means the exiting air dewpoint can't be any higher than 50°F, which reduces high humidity in the OR. Air is then re-heated as needed by the space, either at the terminal box in the duct work or at the central unit, after the chilled water coil before entering the space to control temperature so as not to freeze people. In the winter when it's dry, a humidifier either in the duct work or in the central unit should maintain space humidity. Hope that helps. -Chas