What is your experience with Target type flowmeter? I've used them for flow switches, but not flowmeters.

A hot oil heater vendor wants to install one in their system. We would like an orifice with DP cell. Startup is this weekend and it shows up with a target type flowmeter.

Does fluid density affect the accuracy?

 
Replies continue below

Recommended for you

You have to correct the calculation from DP to flow according to the oil temperature (Density)
Flow = K * Sqrt ( DP * Density)
if you know the flow at specific DP and Density, you can only correct according to the sqrt of the change in density.
Personally, I prefered to use Vortex Flow meter for hot oil if the size of pipe is 6" or less.
 