TiCl4
Chemical
- May 1, 2019
- 631
I'm specifying an iron (iii) chloride (40%) fiberglass storage tank that is filled by the vendor via tanker truck. The tanker truck typically offloads via air pressure, and has a PSV on the tanker truck at 30 psig.
Typically, the vendor trucker will pressurize to ~15 psig, then shut off air supply at 50-70% offload to let the tanker depressurize as liquid level in the tanker truck drops. The over-pressure scenario is if the vendor trucker does not draw down air pressure during offloading, and is pressurized to the maximum allowable when all liquid off-loaded. This will lead to a scenario whereby an large air-surge will go through the pipe and into the tank, necessitating a decent vent size to handle the surge.
FYI we have split other fiberglass tanks nearly in half in the past due to this issue - they were not appropriately sized for the air surge.
I'm in the process of specifying the tank to the vendor for quote. The tank is going to be a fiberglass tank, likely Derakane 411 or similar. I have a few questions/concerns about the overall system design:
1. What is the maximum economical pressure rating for a fiberglass tank (especially a flat-bottom/dome top storage tank?) It is likely cheaper to specify a larger vent than a thicker tank, but I'm not familiar with fiberglass tank pressure rating economics.
2. The current tank to be replaced is bottom entry. Iron chloride has a tendency to foam, and I am concerned that the relief of the 700-1000 SCFM (my initial swag, not detailed calc, ~100 ft of 2" fill pipe) may become two-phase at such a large air flow rate. I'm thinking I should design the system for top entry, but FeCl3 will foam on splash entry. That is not desirable either. Directing liquid flow towards the side of the tank would reduce foaming, but I'm concerned that the solids in the FeCl3 liquid may abrade the surface of the tank if I direct flow towards the side of the tank. Perhaps the best solution would be a bottom feed with a hinged manway (24", perhaps) for relief, accepting that relieving conditions may be two-phase? I'm not sure the best direction to take on this. Help would be appreciated for both tank and relief design options.
Typically, the vendor trucker will pressurize to ~15 psig, then shut off air supply at 50-70% offload to let the tanker depressurize as liquid level in the tanker truck drops. The over-pressure scenario is if the vendor trucker does not draw down air pressure during offloading, and is pressurized to the maximum allowable when all liquid off-loaded. This will lead to a scenario whereby an large air-surge will go through the pipe and into the tank, necessitating a decent vent size to handle the surge.
FYI we have split other fiberglass tanks nearly in half in the past due to this issue - they were not appropriately sized for the air surge.
I'm in the process of specifying the tank to the vendor for quote. The tank is going to be a fiberglass tank, likely Derakane 411 or similar. I have a few questions/concerns about the overall system design:
1. What is the maximum economical pressure rating for a fiberglass tank (especially a flat-bottom/dome top storage tank?) It is likely cheaper to specify a larger vent than a thicker tank, but I'm not familiar with fiberglass tank pressure rating economics.
2. The current tank to be replaced is bottom entry. Iron chloride has a tendency to foam, and I am concerned that the relief of the 700-1000 SCFM (my initial swag, not detailed calc, ~100 ft of 2" fill pipe) may become two-phase at such a large air flow rate. I'm thinking I should design the system for top entry, but FeCl3 will foam on splash entry. That is not desirable either. Directing liquid flow towards the side of the tank would reduce foaming, but I'm concerned that the solids in the FeCl3 liquid may abrade the surface of the tank if I direct flow towards the side of the tank. Perhaps the best solution would be a bottom feed with a hinged manway (24", perhaps) for relief, accepting that relieving conditions may be two-phase? I'm not sure the best direction to take on this. Help would be appreciated for both tank and relief design options.