Hi,
I have received quotes for electric heaters to freeze protect a large water holding tank. One suggetsts a 25 KW (approx 85000 BTU/hr loss) heating requirement & one a 90 KW (approx 307000 BTU/hr loss)heating requirement. it is a 36' diameter x 40' high tank on a concrete slab w/ R-10.2 insulation on the walls and an uninsulated roof. from what i can gather, the ground losses can be neglected at this temperature/tank size. The losses through the walls will be calculated using the following:
(SA(walls) x k x delta T)/3412 BTUh/KWh =
(4524ft^2 x .098 Btu/Hr/ft^2/°F/in(for R10.2) x 42F)/3412 = 5.5 KWh
From the Chromalox catalog (beginning @ page 19):
I can see that the losses from uninsulated steel walls would be calculated using the following:
U x delta T x SA(roof) =
(5.1 BTU/Hr.Sq.Ft.°F (for 15 mph wind) x 42 x PI*18^2)/3412 = 64 KWh
now it would appear that the 90 KW quote is more correct based an including a safety factor & some ground loss value, however if the water is never in direct contact with the roof of the tank, would the air at the top act as insulation(hence the 25 KW requirement)? Obviously there is a large difference in product/operation costs of these units so I would like to know if 25 KW is sufficient or if i should go with the 90 KW to be safe as this is a fire protection tank. All help is appreciated - Thanks!
I have received quotes for electric heaters to freeze protect a large water holding tank. One suggetsts a 25 KW (approx 85000 BTU/hr loss) heating requirement & one a 90 KW (approx 307000 BTU/hr loss)heating requirement. it is a 36' diameter x 40' high tank on a concrete slab w/ R-10.2 insulation on the walls and an uninsulated roof. from what i can gather, the ground losses can be neglected at this temperature/tank size. The losses through the walls will be calculated using the following:
(SA(walls) x k x delta T)/3412 BTUh/KWh =
(4524ft^2 x .098 Btu/Hr/ft^2/°F/in(for R10.2) x 42F)/3412 = 5.5 KWh
From the Chromalox catalog (beginning @ page 19):
I can see that the losses from uninsulated steel walls would be calculated using the following:
U x delta T x SA(roof) =
(5.1 BTU/Hr.Sq.Ft.°F (for 15 mph wind) x 42 x PI*18^2)/3412 = 64 KWh
now it would appear that the 90 KW quote is more correct based an including a safety factor & some ground loss value, however if the water is never in direct contact with the roof of the tank, would the air at the top act as insulation(hence the 25 KW requirement)? Obviously there is a large difference in product/operation costs of these units so I would like to know if 25 KW is sufficient or if i should go with the 90 KW to be safe as this is a fire protection tank. All help is appreciated - Thanks!