tan delta

Status
Not open for further replies.

haisa

Electrical
Oct 17, 2008
26
Hello Engrs
We conducted a tan delta test on a 30MVA, 132/33KV transformer recently using OMICRON CPC 100. At different voltages we had values like -6%, 0.5 % and 23%. What can we deduce from these. Iread that for good insulation the value should be around 0.007%
what does the minus sign imply.
 
Replies continue below

Recommended for you

There's something severely wrong with the measurements. Those numbers are not plausible at all.
Lots of moisture *could* be a reason. But those numbers are all over the place and indicate bad measurement practice. Or faulty equipment.

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
I surmise this is a 2 winding unit and what were you measuring as in what were your connections and test set hook-up ?
 
It's quite possible the Omicron instrument is defective. Got a bad Doble last month.
 