I'm designing the light gage steel for an apartment complex renovation. On one floor, the studs span 22'-4" and have a 12' wide window. I am calculating I need (4) 6", 12ga studs with 2 1/2" flanges to make this work. So my jamb ends up being 10" wide. Seems kind of ridiculous and I end up having to worry about torsion etc. due to the window header and sill only framing into one side of the jamb. At what point should the EOR have specified a tube steel jamb for this condition?
I get this all the time and it drive me nuts. It seems it is done out of ignorance for the limitations of light gage steel and the fact that they want to keep their fee low by delegating the designs to the light gage subcontractor.