"Does anyone else ever tag all manual valves? "
Nuclear power plants might. Years ago I worked on a number of Refinery projects for one specific Client where this question came up.
We finally defined certain criteria for doing it. But it was never done on any of the projects.
Before you start a Valve Numbering Program, you must advise the client to have a clear and meaningful purpose for doing it. They will pay for the initial work and they will go on paying for a very long time. It is time consuming and once started it goes on for the full and complete life of the plant or it is not worth doing at all.
1. Do not number any (non-instrument) valves until the end of the Detail Design phase and the Isometrics have been issued for fabrication.
2. Update all P&ID's for all other marks.
3. Take all clean copies of all P&IDs and all piping isometrics.
4. Create a Valve Numbering data base (excel spreadsheet) to record the following:
- Valve Number
- P&ID Number
- Line Number
- Valve type (Gate, Globe, Plug, Ball, Butterfly, Check, etc.)
- Valve function (Shut-Off), Throttle, etc)
- Commodity (Water, Oil, Acid, etc)
- Valve normal Setting (Open, Closed, etc.)
- Install Status (Original, Replacement, Reconditioned, etc)
- Valve Brand
- Model Number
- Install date
- Last Maintenance Date
- Last Maint. Reason (Replace packing, replace seats, etc )
5. Start the Numbering and go from one end of the process to the other makring the P&IDs, the Isometrics and the Valve list.
6. Send the Number Column of the list to a tag maker. The Tag is to have only the "Number" (no other data).
7. Update the Isometrics and the P&IDs for the added numbers.
8. Establish a Sub-Contractor to do the Valve taging
When the Tags are available and the P&IDs and Isos are ready Issue the Package to the Taging sub-contractor.
9. Have a QA/QC team Follow the Tagging to insure the Tagging is correct. The QA/QC team should be made up of one or more members of the engineering company staff and the Client personnel.
10 Develop a Training module for the Client Maintenance Staff to cover the Valve Numbering policy, Procedure and Purpose.
I hope this helps you or others.
Good luck!