You will need to clarify with the HVAC system designer whether the diffuser is of horizontal or vertical discharge. A.8.3.2.5 provides some clarification. Also Table 8.3.2.5(a) says within the first 1' or 2'-6" from diffuser edge, depending on discharge, sprinklers must be of intermediate temp. classification unless the air temperature does not exceed 100F/38C. The commentary also clarifies that the distances be measured from the outer edge of the heater/duct/diffuser.