Dear Farhad47
My immediate reaction was to say soft start too, but then I got to thinking.
The selection of the type of synchronous motor and the most appropriate starting method depends on more factors than just those in the info you have given. These are quite large motors so it is difficult to be specific without knowing more information. For example:
[ul][li]Are these motors still to be purchased, or are you trying to adapt some existing motors to a new application? [/li]
[li]If they are new motors that you are specifying, put the onus on your suppliers to meet your performance criteria - tell them what to achieve, not how to do it. If you're buying the fan separately, give the fan details to the motor suppliers (e.g., torque speed curves, inertia, etc.) Tell them of your electrical system constraints such as fault level, max permissible voltage dip, intermediate transformer details, etc. If you're buying the fan and motor as a package, the fan supplier will still need to know your system constraints to pass on to his motor subcontractor. [/li]
[li]Have you considered the life cycle cost advantages that you might get from a fully rated variable speed drive? If your process demands variable flow rates from your fans, the improvement in part-load efficiency of a VSD over a constant speed drive can be startling. The incremental capital cost of a VSD vs. a conventional installation can be recovered (in many cases) in two to three years, depending on the amount of part-load running involved. Also, if a fully-rated VSD is an option on this basis, you may be better considering a variable speed induction motor drive instead. [/li]
[li]If they are existing motors, the motor construction may guide you to your solution. If you have synchronous induction motors, you are probably stuck with 2). For reactor starting an SIM, you will probably still have to load the starting winding, which will need the starting resistor. If you just short-circuit the starting sliprings and brushgear, you will likely damage your brushgear and sliprings due to the high current that will flow. You might be able to apply a soft start to an SIM, but you will likely not get away from brushgear totally. [/li]
[li]If you have a conventional brushless synchronous motor, you could probably use either reactor or soft-start. For reactor starting, you would have to study whether you can get enough motor torque to accelerate the fan using the current limitation allowed by the reactor. If you can't get enough torque, you might try autotransformer starting as another option. [/li]
However, my immediate reaction these days would be to say soft start, though you would probably have to modify the brushless exciter (to replace the exciter dc field stator with an induction motor type stator) to allow motor field current to be available at standstill. Again, you might consider a full VSD conversion, but you would need to study the effects of the VSD on the motor (e.g., harmonic currents increasing heating, harmonic torques exciting shaft system and fan critical frequencies, need for separate vent fans) and the supply system (e.g., harmonic currents/voltages causing power quality issues for your other plant and your network service provider). [/li][/ul]
There is no hard and fast rule that says one solution is better than another for any motor of this type and size. Each application is different, and it really does depend on more than just the motor size as to which is the best solution. You need to address all of these peripheral issues, or have your supplier address them before homing in on your final solution.
PS I do not work for a motor or drives supplier, so I'm not touting for business here - I've just been there and done that in the past.