There is an alternative. For rather large, forgot the exact size, Asplund refiner motors (in pulp industry) I had an interesting experience with 11 kV synchronous motors where we used a "pony motor without motor".
The idea was that we should apply a fraction of rated power by using a 690 V PWM VFD to slowly bring the speed up so the machine could be connected to 11 kV without the large transient you usually get when starting via the amortisseur winding.
It worked astoningishly well and we were able to start those rather large machines from a 690 V grid fed by a 1600 kVA transformer without seeing much dip in the light or disturbing other equipment. The VFD was a Siemens MasterDrive rated at 850 kW. It could deliver around 50 % above rated for the time needed to bring the machine up to speed. We needed that.
At 690 V, the torque is around 0.4% of rated torque and that is too low to even think about a direct connection. So, we put a small 690/3300 V transformer between VFD and motor. The thermal time constant of a transformer is such, that we could use a rather small one. I do not have all data available, but I think we got away with a 250 kVA transformer.
There were several defibrators and we used the VFD/transformer combination to start them. The 11 kV breaker was placed in the same panel as the main breaker. And, yes, there were fuses. We thought about leaving them out, but the electro-boss said that he liked his job better than the money we could save on leaving the fuses out.
Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.