power2engineer
Electrical
In our plant we have 4.16KV 5500HP, 0.8PF leading Brushless synchronous motor with manual exciter regulator for reciprocating compressor drive. When motor was started at noload after upgrading the relay protection system I observed strange thing. The motor rated field Amps is 5.8 Amps. We started the motor with 2.5A field current applied it sychronized but the stator amps was flucting between 70A-130A and Power factor was also fulctuating between 0.3-0.5 Leading. Varying the field current at 2.0A and 3.5A we observed similar results. After applying 25% load the stator current and Power factor stabilized can anybody explain this Phenomena? Thanks