On such a large machine the mechanical limitations of the machine at least need to be considered. 15% increase in output power is substantial.
Further to ePete's post, the heavily over-excited condition will probably be limited by the rotor reaching its thermal limit. In the severely under-excited condition, the stability limit of the machine will be reached. The stability limit will depend upon shaft loading. It is quite improbable that a motor would be operated at either of these extremes, so the limits are largely theoretical rather than likely to be encountered in operation.
There are a lot of similarities in the capability curves of synchronous motors and synchronous generators. Discussion of generator curves seems to be more common.
----------------------------------