I am tasked with designing a PID control strategy for a system that will use fluid power to turn the shaft of a synchronous generator. My question is whether my planned control strategy will work, and specifically, will my two PID loops interact and therefore not work well.
The generator will be connected to the local grid. The fluid power will be created by a new innovative system that extracts energy from the temperature differential of hot water heated by a massive solar array and cold sea water and creates pressured flow of hydraulic oil. The fluid power from the hydraulic oil will be transferred by using it to spin the shaft of a synchronous generator. Before turning the shaft it passes through a control valve.
There are two measured variables: Kilowatts (kW) and power factor (PF) are measured at a control device where the power is transferred to the grid and are available to our control system as 4-20mA input signals. There are two control variables our control system can manipulate with analog outputs: the position of the control valve that regulates flow of the hydraulic oil, and the excitation current to the synchronous generator.
CONTROL LOOPS:
1. Kilowatt (kW) controller whose PV is kilowatts (available as an analog input from the device connecting the generator to the grid) and whose CV is the position of the valve allowing fluid power to be delivered to the generator shaft. (The setpoint is 250kW which is what the generator is designed to produce.) This will be a relatively slow acting loop.
2. Power Factor (PF) controller whose PV is the power factor (available as an analog input) and whose CV is the excitation current to the synchronous generator. This will be a relatively fast acting loop.
CONTROL STRATEGY:
• Ramp open the valve until the generator RPM is at the design point (1800). No excitation is applied to the generator and the generator is not connected to the grid yet.
• Apply a specified excitation and put the generator online.
• With the kW controller in manual, ramp open the valve slowly to a specified value (say 80%) that is known from design and experimental confirmation to result in 250kW. During this time the excitation controller is allowed to operate in auto. It is expected that it will raise the excitation current as valve opens and kW increases. So in effect, both the valve position and excitation are ramped up.
• The kW controller is placed in auto. When cloud cover results in slowly dropping kW, the KW controller will slowly open the valve. When fluid power recovers due to restored sunlight the KW controller will slowly close the valve. It is expected that the PF controller will not interact with the kW controller since the latter is slow acting.
• Additional algorithms will determine when to take the generator offline, usually due to nightfall.
The generator will be connected to the local grid. The fluid power will be created by a new innovative system that extracts energy from the temperature differential of hot water heated by a massive solar array and cold sea water and creates pressured flow of hydraulic oil. The fluid power from the hydraulic oil will be transferred by using it to spin the shaft of a synchronous generator. Before turning the shaft it passes through a control valve.
There are two measured variables: Kilowatts (kW) and power factor (PF) are measured at a control device where the power is transferred to the grid and are available to our control system as 4-20mA input signals. There are two control variables our control system can manipulate with analog outputs: the position of the control valve that regulates flow of the hydraulic oil, and the excitation current to the synchronous generator.
CONTROL LOOPS:
1. Kilowatt (kW) controller whose PV is kilowatts (available as an analog input from the device connecting the generator to the grid) and whose CV is the position of the valve allowing fluid power to be delivered to the generator shaft. (The setpoint is 250kW which is what the generator is designed to produce.) This will be a relatively slow acting loop.
2. Power Factor (PF) controller whose PV is the power factor (available as an analog input) and whose CV is the excitation current to the synchronous generator. This will be a relatively fast acting loop.
CONTROL STRATEGY:
• Ramp open the valve until the generator RPM is at the design point (1800). No excitation is applied to the generator and the generator is not connected to the grid yet.
• Apply a specified excitation and put the generator online.
• With the kW controller in manual, ramp open the valve slowly to a specified value (say 80%) that is known from design and experimental confirmation to result in 250kW. During this time the excitation controller is allowed to operate in auto. It is expected that it will raise the excitation current as valve opens and kW increases. So in effect, both the valve position and excitation are ramped up.
• The kW controller is placed in auto. When cloud cover results in slowly dropping kW, the KW controller will slowly open the valve. When fluid power recovers due to restored sunlight the KW controller will slowly close the valve. It is expected that the PF controller will not interact with the kW controller since the latter is slow acting.
• Additional algorithms will determine when to take the generator offline, usually due to nightfall.