Even as we were corresponding thru Eng-Tips,I was carrying out the installation work (cabling, control wiring etc.)at the site. Yesterday, I commissioned the set (180 KVA, 415V, 3 phase) by synchronizing it with the existing 3 x 500 KVA sets. I am glad to report that the set ran for over 4 hours in a synchronised state without ever tripping. As the load sharing is being done manually, I tried to load the 180 KVA set but could raise it to only to 90 KW. At this loading, it was drawing a current of 200 Amps. This ampere load remained fairly constant even as I decreased the KW load even to 20kW ! I am still scratching my head over that !
I have asked for the governer to be calliberated afresh
( mainly to give me time to think of a viable load sharing scheme ! )
Well, thanks to jbartos & peterb for their interest and without whose prompt replies, I would be still groping in the dark.