deltawhy
Electrical
- Jun 1, 2011
- 95
Hello,
I have a question regarding synchronizing a small generator with the utility. I have a 15kW genset that a client wants to sync to the utility feeding his building. The synchronization can be done using a contactor and a synchronizing controller (like easygen or woodward EGCP-2). My question is more based on theory of operation. Will the generator be able to feed the building loads (about 8kW), or will the utility be providing for all the required loads? I did a very quick load flow analysis on etap and it showed my generator feeding 0kW, 0kvar, while the utility covered the entire load. Is there any way to ensure my genset will be providing at least 50% of the building load, while the utility covers the other 50%?
Thanks.
I have a question regarding synchronizing a small generator with the utility. I have a 15kW genset that a client wants to sync to the utility feeding his building. The synchronization can be done using a contactor and a synchronizing controller (like easygen or woodward EGCP-2). My question is more based on theory of operation. Will the generator be able to feed the building loads (about 8kW), or will the utility be providing for all the required loads? I did a very quick load flow analysis on etap and it showed my generator feeding 0kW, 0kvar, while the utility covered the entire load. Is there any way to ensure my genset will be providing at least 50% of the building load, while the utility covers the other 50%?