odlanor
Electrical
- Jun 28, 2009
- 689
The powerplant has a transformer of 230kV-13.8-13.8kV
Each generator can absorb 1 / 4 of the reactive line.
The best sequence of operation to dispatch generation would be:
1 -starting and excitation the 1 generator-transformer unloaded.
2 - 13.8 kV synchronizing of the 3 generators.
obs: governors should have a speed droop 4 to 5% to allow parallel operation of generators to reduce circulating current between generators.
3-Synchronizing the transformer with the 230kV line.
obs: is it possible,with setpoints control of only 1 generator ?
5-dispatch generation using joint control of the power regulation of generators.
Anyone have any experience with this problem?
Each generator can absorb 1 / 4 of the reactive line.
The best sequence of operation to dispatch generation would be:
1 -starting and excitation the 1 generator-transformer unloaded.
2 - 13.8 kV synchronizing of the 3 generators.
obs: governors should have a speed droop 4 to 5% to allow parallel operation of generators to reduce circulating current between generators.
3-Synchronizing the transformer with the 230kV line.
obs: is it possible,with setpoints control of only 1 generator ?
5-dispatch generation using joint control of the power regulation of generators.
Anyone have any experience with this problem?