dlineh
Electrical
- May 23, 2009
- 3
I would appreciate any advice on a potentially hazardous situation we have been experiencing during switching operations. While breaking a station tie on a 23kv system utilizing three single 900 amp solid blade disconnects we are experiencing some undesireable failures on several different feeders. We are breaking station ties between two stations fed by two different transmission voltages (140kv and 238kv)on a distribtion voltage of 23kv using the S&C Loadbuster tool. On a great deal of occassions the tool has failed, sometimes totally destroying and melting the tool. We have worked extensively with S&C and it is not the fault of the tool or lack of maintenance. Could the leading power factor create some type of transient that would cause the tools failure? Would some type of gang operated switch resolve this issue? If so what would you reccommend? So far the injuries have been minor as a result of the switching failures. The regulators at the station have been addressed before switching. The "obvious" switching hazards have been adddressed and we are still experiencing the same problem without any pattern. The switching operations failures are never consistant. Thanks for any advice.