In answer to your question regarding the 30kA for 3s.
This is simply the rated short time current of the of the board (busbars etc.). The amount of current that the board can handle depends on the duration of the fault i.e. k=I^2t = 2700kA^2s. If the max. fault duration was 2s then rated short time current(2s) = sqrt(2700/2) = 36,7kA for 2s.
What is normally more important than the above is the 'make' and 'break' ratings of the circuit breakers. The 'break' rating would typically be the same as the rated short time current (30kArms) and the make on an IEC breaker would typically be 2,5 x 'break' = 75kApeak.
Careful consideration needs to be given to the asymmetry during the fault and any contribution from large motors. It is no good using steady state fault currents if the protection will trip instantaneously.
In other words be VERY careful.
The most cost effective solution would probably be fault limiting reactors. As mentioned in another post volt drop needs to be considered, although this should not be a problem unless large motors are being started DOL (still, it needs to be considered). A calculation of the cost of the reactor losses should also be carried out before a decision is made.
Current limiters are very expensive and tend to compromise protection grading.
As an outside chance, are there no bus sections that can be run open ?