It is about busbar proptection of HV(22kV) board ,where all circuits except station service transformer circuit have dedicated CTs for high impedance based bus protection scheme. Station service trf bay is switch fuse unit without CT. Appropriate fuse can be choosen to make sure that BZ scheme do not operate for external fault(i.e. on station service trf HV or LV side) but for real internal bus fault , how do you make sure that fuse blows to isolate faulty bus ?