During a recent cleaning, we found some internal cabling that had insulation issues (see file). The cabling is from the load cables to the contactors (Cutler-Hammer), voltage level is 6.6 kV, the conactors are pretty much closed all the time so no frequent load spikes to speak of, and loading is well below capacity of these conductors. Initial assesment is low energy electrical arcing, corona discharge, and tracking as a reasult of no outer
semi conducting shield. These cables intended use is listed as temporary installation around damaged cables or for temporary power sources. They come with the cubicles, so I never gave them a second thought. Until now!