Asixth,
Don't believe everything you read in technical papers, especially when they are produced by someone trying to sell something. There is too much logical arguement, from people who do not benefit either way from the arguement, against its use to risk using it. As I pointed out in an earlier posting my calculations show it to be inadequate and agree with test data, without having to go into
RE shear, interestingly some other codes have gone the other way, I think it is the Canadian code (from memory) that specifically precludes the use of low ductility steel for shear, while AS3600 still allows it.
I know they are cuurrently having the same arguements as us against Low Ductility reinforcement in Europe, and their minimum strain is 2.5% while ours is much worse at 1.5%.
RE the analysis,
That is just regurgitating the standard AS3600 rule that allows everything to be be based on an elastic analysis and as OzEng80 has suggested, it also fits in with the logic of no redistribution. Unfortunately redistribution occurs in all slabs as they crack during the loading cycle, even if you do not allow for it in design.
Design to analysis is different and cracking must be allowed for deflections. However, if you are using FEM analysis and start trying to reanalyse for cracked sections for deflections, what properties do you consider cracked values for? Obviously bending stiffness, but what about torsional stiffness and column stiffness. That is where current FEM design programs are still not telling all. What are they assuming to be cracked, only the slabs bending stiffness?? If you are going to start doing this then you also have to start allowing for creep and shrinkage in the cracked analysis and also construction seguence. All too difficult.